Content
Code references
Added by Hva Skjer ago
Indiana code base of:
-
ASME A17.1 (2007)
-
Indiana Building Code (IBC 2014)
-
International Building Code (IBC 2012)
-
NFPA 70 (NEC 2008)
-
NFPA 72 (2010)
The following is an in-general R-1 & R-2 occupied building quick check. For I, A, etc. class buildings some of this code does not apply and one will also need to refer to additional code.
Rise based
4 floors:
- Hoistway ventilation required.
- Accommodate an ambulance stretcher.
- Enclosed lobby with smoke/fire partition (unless building is protected by an automatic sprinkler system [I-2 & I-3 are not exempt]). Note: IBC 713.14.1
5 floors:
- Standby (emergency) power required (generator with transfer switch, not battery lowering).
|
IBC - 1007.2.1 Elevators required. In buildings where a required accessible floor is four or more stories above or below a level of exit discharge, at least one required accessible means of egress shall be an elevator complying with Section 1007.4.
|
IBC - 1007.4 Elevators. In order to be considered part of an accessible means of egress, an elevator shall comply with the emergency operation and signaling device requirements of Section 2.27 of ASME A17.1. Standby power shall be provided in accordance with Chapter 27 and Section 3003. The elevator shall be accessed from either an area of refuge complying with Section 1007.6 or a horizontal exit. |
60 feet of rise:
- Lobby phone required.
75 feet of occupied rise (HIGH-RISE BUILDING):
- Enclosed lobby with smoke/fire partition (even if an automatic sprinkler system is used). Note: IBC 713.14.1
- Remote Fire Status Panel located in the fire command center. IBC 403.4.6, 911.1.5 (1), (4), (13.4), (17) & (18)
- Emergency power is required.
- Emergency power must also power the remote fire status panel.
100 feet of rise:
- Alarm bell (secondary) required.
120 420 feet of rise:
- Fire service access elevator required [IBC 403.6.1 and Section 3007].
- Fire service access elevator lobby.
Note: IBC 403.6.1 Fire service access elevator. In buildings with an occupied floor more than 120 feet (36 576 mm) 420 feet (128 000 mm) above the lowest level of fire department vehicle access, no fewer than two one fire service access elevators, or all elevators, whichever is less, shall be provided in accordance with Section 3007. Each fire service access elevator shall have a capacity of not less than 3500 pounds (1588 kg). [Includes Indiana’s IBC 2014 amendments]
Reference code:
Accommodate an ambulance stretcher [IBC 3002.4]:
The elevator car shall be of such a size and arrangement to accommodate an ambulance stretcher 24 inches by 84 inches (610 mm by 2134 mm) with not less than 5-inch (127 mm) radius corners, in the horizontal, open position and shall be identified by the international symbol for emergency medical services (star of life). The symbol shall not be less than 3 inches (76 mm) in height and shall be placed inside on both sides of the hoistway door frame.
- 4 or more stories above or below grade plane.
- 3 stories or less in height in buildings of I-1, I-2, I-3, and R-4 occupancy.
Alarm bell (secondary) [ASME A17.1 2.27.1.2]:
-
Required when the elevator rise is 100 feet or more.
-
have a rated sound pressure rating of not less than 80 dBA nor greater than 90 dBA at (10 ft)
Vertical Changes in Level: Changes in level up to 1/4 inch (6.4 mm) high maximum are permitted to be vertical (Section 303.2).
Beveling [ADA 303]:
The 2010 ADA Standards for Accessible Design specifies beveling requirements for changes in level on accessible routes.
The relevant section is 303 Changes in Level, specifically 303.3 Beveled:
-
Vertical Changes in Level: Changes in level up to 1/4 inch (6.4 mm) high maximum are permitted to be vertical (Section 303.2).
-
Beveled Changes in Level: Changes in level between 1/4 inch (6.4 mm) high minimum and 1/2 inch (13 mm) high maximum shall be beveled with a slope not steeper than 1:2.
Blind Hoistway (If sill to sill is 36 feet or greater) [ASME A17.1 2.11.1.2]:
-
Self-closing, self-locking emergency door installed with a minimum clear opening of 28x80 inches.
-
Door marked “DANGER, ELEVATOR HOISTWAY”.
-
Door safety switch installed and tied into the safety circuit.
-
Cylinder lock installed with a minimum of 5 pins/5 discs.
-
Door must open without a key from the hoistway.
-
Key must be removable only in the locked position.
-
Key must be of group 1 security, dedicated to blind hoistway doors only and secured into the firebox.
-
A hinged self-closing barrier independent of the door shall be installed horizontally across the entrance on the hoistway side at a height of 42 inches.
-
Door and barrier must not open into the hoistway.
Canting [ASME A17.1 2.1.6.2]:
- Other than separator beams between adjacent elevators, all projections/recessions 4 inches or greater in depth and greater than 1 inch in width are to be beveled at an angle of not less than 75 degrees.
|
Quick math: for 75° angle: Find your pocket depth.
|
Hoistway vents required [IBC 3004.1-3004.3]:
Note: Vent must be mechanically held open and powered shut. Vent must open when the elevator enters fire service.
- Occupied building penetrating more than three stories (i.e., 4 or more stories.)
Lobby phone [ASME A17.1 2.27.1.1.4]:
- Required when the elevator rise is 60 feet or more.
Refuge space top of car [ASME A17.1 2.4.12.1]:
- Must be a minimum of 43 inches vertical with the car at its maximum travel distance.
Shunt trips [IBC 3006.5] [NFPA 72 6.16.4.1 – 6.16.4.5]:
If water can hit our controller and/or machine the following are required:
-
Heat detector, located within 2 feet of the sprinkler head. Must be set to a lower temperature rating than the sprinkler head.
-
Shunt trip, must not be self-resetting. Must be delayed (timed relay) for a period greater than the elevator fire-recall period.
Stop switch, pit (secondary) [ASME A17.1 2.2.6.2]
- When the pit exceeds 1 700 mm (67 in.) in depth, an additional stop switch is required adjacent to the pit ladder and approximately 1 200 mm (47 in.) above the pit floor.
Relay contacts:
-
Emergency power contacts are – Dry, normally open.
-
Fire service contacts – Dry, normally open, powered closed. Open on activation or power loss.
-
Security (card reader) contacts are – Dry, normally closed.
Residency examples:
I [IBC section 308]: |
R [IBC section 310]: |
I-1: (more than 16 persons) Assisted living facilities, group homes |
R-1: Hotels, motels |
I-2: Hospitals, nursing homes |
R-2: Apartment houses, dormitories |
I-3: Correction centers, detention centers |
R-3 Boarding houses with 16 or fewer occupants |
I-4: Adult day care, child day care |
R-4: (16 or fewer persons) Assisted living facilities, group homes |
Current codes: https://www.in.gov/dhs/fire-and-building-safety/fpbsc-rules/
2007 ASME A17.1 |
2009 Indiana Electric Code (2008 NFPA 70) |
2010 NFPA 72 |
2014 Indiana Building Code |
Electrical:
Disconnects
Disconnect working spaceNFPA 70 – 110.26 (A)(1), (A)(2), (A)(3). | ||||||||||||
|---|---|---|---|---|---|---|---|---|---|---|---|---|
|
depth;
Note: concrete, brick and tile walls are considered grounded. | ||||||||||||
|
width;
| ||||||||||||
|
height;
| ||||||||||||
Disconnect fusing: | ||||||||||||
Note: All primary elevator companies ship traveling cables with 14 AWG wiring for their 120v circuit. |
Illumination/GFCI: |
|---|
|
Pit
|
|
Machine space / Control space
|
|
Lobbies
|
|
Elevator itself
|
|
The state has recognized the particular circumstances surrounding MRL elevators (ICS in Kone's case) in regards to 2007 code.
As a result, both code sections must be complied with. |
Smoke detectors:
Lobbies:
-
Each lobby must have an initiating device.
-
Location: Horizontal plane; within 21' --- Vertical plane; ceiling height equal or less than 15'
-
Note: If a lobby contains more than 1 smoke detector, only 1 of them is required as an initiating device as long as it is within the location scope of all elevators in the bank (21'/15'). The rest of them need only be general area detectors.
|
NFPA 72 - 21.3.5 A lobby smoke detector shall be located on the ceiling within 21 ft (6.4 m) of the centerline of each elevator door within the elevator bank under control of the detector. |
- If ceiling height is greater than 15' a wall mounted smoke detector is normally installed within 60" above the entrance. Note: code only dictates close proximity, newer code states 60" which is what the inspectors like to go by as a reference point.
NFPA 72 (2010) - 17.7.3.1.4* If the intent is to initiate action when smoke/fire threatens a specific object or space, the detector shall be permitted to be installed in close proximity to that object or space. |
- Reasoning: due to the recognition of smoke stratification: (where smoke stops rising because it loses buoyancy).
Machine Room/Space; Control Room/Space:
- One must be present
ASME A17.1 (2007) - 2.27.3.2.1 In jurisdictions not enforcing the NBCC, fire alarm initiating devices used to initiate Phase I Emergency Recall Operation shall be installed in conformance with the requirements of NFPA 72,and shall be located |
Hoistway (shaft):
- If this is a MRL (Machine Room-less elevator[ICS]) a smoke detector MUST be installed at the top of the hoistway. This is machine space and trumps NFPA 72 - 21.3.6
NFPA 72 - 21.3.6 Smoke detectors shall not be installed in unsprinklered elevator hoistways unless they are installed to activate the elevator hoistway smoke relief equipment. |
In general:
Airflow near smoke detectors:
- Smoke detectors must be clear of HVAC registers by a minimum of 3’.
NFPA 72 - 17.7.4.1* In spaces served by air-handling systems, detectors shall not be located where airflow prevents operation of the detectors. |
- Even though specifically 3’ does not exist for commercial, Authority Having Jurisdictions (AHJs) recognize and enforce the minimum of 3’ based off residential code.
|
NFPA 72 - 29.8.3.4 Specific Location Requirements. (6) Smoke alarms and smoke detectors shall not be installed within a 36 in. (910 mm) horizontal path from the supply registers of a forced air heating or cooling system and shall be installed outside of the direct airflow from those registers. |